When troubleshooting a loop, an LCR meter at the pull-box reads about half the expected loop inductance. What is the most likely problem?

  1. A second loop is paralleled by mistake or a saw-cut crossover
  2. The detector amp is overheating
  3. AC line voltage is high
  4. The pedestrian pushbutton is stuck

Answer: A — A second loop is paralleled by mistake or a saw-cut crossover

The correct answer is shown above. Try the full quiz for additional practice.